Separate energy, reserves and frequency services
Energy delivery, spare headroom and enabled frequency response are not interchangeable. A service requires the appropriate direction, speed, measurement and technical qualification. Stored energy and operating point can limit simultaneous energy and FCAS delivery.
The lesson
7 chaptersBrowse the chapters
01One system, ten frequency-control services
The question
What is being bought when a participant is enabled for FCAS?
Mechanism
Energy dispatch determines a power trajectory. Frequency control ancillary services procure specified response capability around that trajectory. Regulation services continuously correct small imbalances; contingency services respond to disturbances. A market label is not a licence to substitute one response characteristic for another.
The NEM has regulating raise and lower, plus very-fast, fast, slow and delayed contingency raise and lower services. The familiar 1-second, 6-second, 60-second and 5-minute labels are a starting vocabulary. Qualification, measurement and delivery obligations come from MASS and the applicable procedures, not from a single timing label.
Keep three ledgers: scheduled energy, enabled ancillary-service capacity and measured physical response. A participant can be enabled without an event demanding its full response. It cannot infer available services merely from the nameplate MW on a battery brochure.
Worked numbers
Two regulation services + four contingency timescales × two directions = ten services. A hypothetical 12 MW enablement for five minutes represents 1 MW·h of reserved capability, not proof of 1 MWh of additional energy delivered.
Try it in the workspace
Open the FCAS capability desk. Explain what each MW input measures before changing it.
02Read the trapezium before adding revenue
The question
Can the same unit offer its maximum FCAS at every energy output?
Mechanism
A service capability curve uses enablement minimum, low breakpoint, high breakpoint, enablement maximum and maximum availability. Within a simplified trapezium, the available service rises along the lower edge, stays flat between breakpoints, and falls along the upper edge. This links energy output to service capability.
For our teaching unit use minimum 10, low 30, high 70 and maximum 100 MW, with maximum reserve 40 MW. This is a fixed-energy, single-service illustration. Real dispatch also applies joint constraints, service-specific parameters, ramping and other requirements.
Calculate both sloping edges and the flat maximum, then take the non-negative minimum. A stated 40 MW maximum is not an instruction to enable 40 MW everywhere. Outputs outside the enablement range produce zero service in this model.
Worked numbers
At 20 MW energy: 40 × (20 − 10)/(30 − 10) = 20 MW. At 60 MW: 40 MW. At 80 MW: 40 × (100 − 80)/(100 − 70) = 26.67 MW before shared headroom.
Try it in the workspace
Select the Low edge and High output scenarios. Predict capability before revealing the results.
03Capability, headroom and the cost of replacement
The question
Which restriction actually limits the reserve offer?
Mechanism
At a fixed energy output, the teaching desk applies both the trapezium and a shared nameplate headroom limit. Unit A's usable reserve is the smaller of those two values. The second provider has separately specified available reserve; the desk does not infer its energy schedule.
At 80 MW energy and 100 MW physical availability, headroom is 20 MW. Although the trapezium permits 26.67 MW, the combined bound permits only 20 MW. Reducing energy can create headroom, but it may move the unit down the other side of the trapezium. More headroom alone does not guarantee more FCAS.
The desk holds energy fixed and buys the cheaper reserve first. It is not a co-optimiser: it does not trade energy redispatch against FCAS procurement cost. Return to Topic 14 for that opportunity-cost mechanism, then identify which joint constraints a production model would need.
Worked numbers
Base energy 60: A supplies 40 MW at A$5/MW/h and B supplies 10 at A$20/MW/h. Offer cost is A$400/h. At energy 80, A supplies 20 and B supplies 30: A$700/h.
Try it in the workspace
Change energy from 60 to 80 MW with reserve demand fixed at 50. Identify the extra provider and the A$300/h cost change.
04A marginal increment is not an average bill
The question
How much does one additional MW of required reserve cost?
Mechanism
Once cheaper reserve has been used, an additional requirement is supplied by the next feasible provider. The desk resolves the fixed-energy allocation for requirement plus one MW. Its cost difference is a finite incremental cost under the displayed assumptions.
In the base case, A is already at 40 MW capability and B supplies 10. An extra MW comes from B at A$20/MW/h. The average procurement cost is A$400/50 = A$8/MW/h; it does not determine the incremental cost. Neither figure is claimed to be a published NEM FCAS price.
If the requirement exceeds total capability, show a shortfall and withhold the marginal-price interpretation. A penalty could make an optimisation model solvable mathematically, but it would not create a physical response. Near a breakpoint, a finite one-MW step can straddle more than one marginal segment.
Worked numbers
Base cost A$400/h; requirement 51 MW costs A$420/h. At energy 80 with only 5 MW from B, a 50 MW requirement leaves 25 MW unavailable.
Try it in the workspace
Select Reserve shortfall. Explain why the desk displays no feasible incremental cost rather than inventing an FCAS price.
05Reserve adequacy is not an eleventh FCAS market
The question
Does an LOR notice mean load is already being shed?
Mechanism
Lack-of-reserve notices describe reserve conditions across the operational horizon. Read the region, forecast or actual status, period, threshold and update time. A forecast notice is not evidence that customers have already lost supply.
Short-term reserve assessment accounts for credible contingencies and forecast uncertainty. It is not simply 'installed MW minus demand', nor can an analyst apply a single fixed percentage to every interval. A service-capability shortfall in our desk does not calculate an LOR level.
RERT uses contracted emergency reserve under its own eligibility, procurement and activation arrangements. It is not one of the ten FCAS markets, and an LOR notice does not prove RERT has been activated. Keep reserve condition, operational decision and observed outcome in separate columns.
Worked numbers
Illustrative screening only: 900 MW available against 850 MW demand leaves 50 MW before contingency and uncertainty requirements. That subtraction alone cannot classify LOR or establish security.
Try it in the workspace
Write a three-row evidence ledger: forecast notice, intervention decision, measured outcome. State which source verifies each row.
06Read actual service prices without inventing an asset's earnings
The question
What can five regional price records tell us?
Mechanism
The evidence lab reads the preserved AEMO DISPATCH/PRICE v5 header and five records for 18 October 2026, 12:45 market time. It selects intervention=0 and exposes ten FCAS price fields with price-status and administered-pricing/suspension flags. These are dated observations, not a current feed.
Start with NSW1: the published raise-regulation price is 1.44; the very-fast raise price is 0.01. For an explicitly hypothetical 12 MW enabled throughout five minutes, the unadjusted service-value illustrations are A$1.44 and A$0.01 respectively. The chosen 12 MW is not an observed unit enablement.
To reconstruct real earnings, obtain matching unit-level enablements and applicable service, region, run, interval, revisions and settlement rules. Do not apply all ten prices to the same MW without proving simultaneous feasible capability and the applicable treatment.
Worked numbers
12 × 5/60 × 1.44 = A$1.44; 12 × 5/60 × 0.01 = A$0.01. The common multiplier equals one MW·h, not one MWh of measured response.
Try it in the workspace
Load the real snapshot in Apply it, choose NSW1 and compare the two fields. Export the evidence record and list the missing unit data.
07What changes—and what needs a new review
The question
Which version of a technical document governs the interpretation?
Mechanism
MASS v8.2 and the FCAS Model in NEMDE v3.0 are both effective 3 June 2024 in the current official register. Very-fast FCAS began in October 2023, but local requirements and transitional limits have continued to change. A launch-date fact is not a timeless operating limit.
The AEMO very-fast transition page includes local updates from June 2026. Do not preserve an old universal 50 MW limit in a model as if it applies everywhere today. Read location, islanding condition, service direction and commencement before using a listed limit.
Finish with a versioned recommendation: what the fixed-energy model establishes, which actual prices were observed, and what would require a full joint-dispatch or compliance review. This course does not authorise market offers or certify delivery performance.
Worked numbers
A hypothetical 12 MW enablement remains a modelling assumption even when paired with a genuine published price. Replacing a price source does not validate the other inputs.
Try it in the workspace
Compare your exported evidence record with the source register. Check schema version, interval, service name and the date due for review.
Watch the explanation
Key terms in plain English
- Current
- Flow of electric charge, measured in amperes. In the circuit context it is different from the amount of energy used over a period.
- MW
- Megawatt: a measure of power, or how quickly energy is transferred. A plant's maximum MW is not its actual output in every interval.
- FCAS
- Frequency control ancillary services: services used to help manage system frequency. They are distinct from the energy traded in MWh.