TOPIC 5 · IN-DEPTH TOPIC

Storage, flexibility and demand response

Compare duration, response speed and operating limits.

Understand · 1 of 4Self-paced

Can you deliver the next three hours?

A site needs 20 MW less grid import through the evening. Work out whether stored energy and a temporary reduction in customer demand can meet the commitment—and be ready when called again.

Read · work through an example · try it yourselfWatch the video
INTERACTIVE · BATTERY DISPATCH

Can the battery cover the peak?

Supply three one-hour demand blocks without exceeding a 40 MW grid-import limit. Adjust battery power and starting energy.

020406080MW20 MWHour 145 MWHour 265 MWHour 3
GridBatteryUncovered demand

Dashed line: grid-import limit. Brown is demand this plan cannot supply within the limit—not a forecast blackout.

Energy is already usable AC-delivered MWh. No recharge during this event; no additional loss deduction.

All demand covered0 MWh gap
Energy left after hour 30 MWh

The simplified schedule meets the import limit.

Check the hourly dispatch
Average MW in each one-hour interval; remaining energy in usable AC-delivered MWh
HourDemand MWGrid MWBattery MWGap MWEnergy left MWh
120200030
245405025
365402500

For this exact sequence, the minimum is 25 MW and 30 MWh. Dispatch each hour is limited by required reduction, available MW and remaining MWh ÷ hours. This is a feasibility check, not a price-optimising dispatch model.

A 20 MW / 60 MWh battery still falls short. What fixes its bottleneck?

Original synthetic case. Before using a schedule at work, check ramping, state-of-charge limits, auxiliaries, temperature, reserve obligations, outage risk and recovery for the next event.

The lesson

10 chapters
Browse the chapters
01Specify the service before choosing the asset

The evening commitment

A site must reduce its grid import by 20 MW from 18:00 to 21:00. It can use a battery behind the meter, reduce some production temporarily, or combine both. A battery sales sheet says 30 MW. Is that enough? You need a duration, an energy boundary and a recovery plan before you can answer.

Turn the request into something measurable

  1. 01
    Where and when?

    Specify the connection meter, start time, notice period and response deadline. Flexibility in another location may not relieve this constraint.

  2. 02
    How much and how long?

    State the reduction in MW and the event length. Here, 20 MW for three hours means 60 MWh of import reduction.

  3. 03
    What happens afterwards?

    State how the store recharges or production catches up, and when another call must be possible.

This is an original site-level teaching case, not a real dispatch instruction or a named market-service specification.
Three different requirements
NeedMeasureDo not assume
Respond quicklyDelay and ramp rateFast controls guarantee sufficient stored energy
Sustain deliveryMW across the whole eventA nameplate MWh rating is all available now
Be ready againRecovery time and end inventoryThe asset starts full again tomorrow

Check your understanding

A 30 MW / 40 MWh usable-delivered battery is offered for the 20 MW, three-hour commitment. Is it sufficient alone?

Show reasoning

No. It has enough power, but only two hours of energy at 20 MW.

40 MWh ÷ 20 MW = 2 h. The commitment requires 60 MWh, so it is 20 MWh short before considering other limits.

Watch the explanation

Key terms in plain English
MW
Megawatt: a measure of power, or how quickly energy is transferred. A plant's maximum MW is not its actual output in every interval.
MWh
Megawatt-hour: a quantity of energy. A steady 1 MW for one hour delivers 1 MWh.
Supporting diagrams

One complete storage cycle

Declare where each energy quantity is measured.

  1. 01 · AC input100 MWh

    Charging efficiency 90%

  2. 02 · Stored internally90 MWh

    Discharge efficiency 90%

  3. 03 · AC output81 MWh

    Round-trip efficiency 81%

Synthetic full-cycle balance, no additional auxiliary loss or inventory change. The two 90% conversion efficiencies multiply; they do not add.